How to stop pump when ABB ACS580 drive switch from remote to local?
I use EFB for control drive in remote state.
When I switch from remote to local , drive switched but reference frequency dont change.
Normally in this state output frequency must be set to zero.
How can I fix this?
When I switch from remote to local , drive switched but reference frequency dont change.
Normally in this state output frequency must be set to zero.
How can I fix this?
Answers
Remember that there are 2 references in the equipment, one for local and one for remote, if an analog signal 1 for example is as a reference in both, the reference will be the same.