how should i get the hart device temperature from hart communication
we use 800xa 6.0.3 and s800 io pm864.
1. now we want to get the hart device information, like device temperature,model, pv......
2. can i display these information on HMI?
but we don't know where to find the hart file(dtm), we ask local abb support, they don't know where or how to get it exactly .
please someone help us?
Answers
You can view the HART device information in DTM. Start with Basic HART DTM. Search for documents :3BDD011939-600_en_Device_Management_Basic_HART_DTM
and 3BDD011934-600_A_en_System_800xA_6.0_Device_Management_PROFIBUS_and_HART_Config
uration.
To install HART functionality select "Device Management PROFIBUS and HART" in system configuration console.
HART Information can be displayed only in a DTM and not in HMI if HART device is connected to S800 I/O.
With S900 I/O you can display secondary HART variables in HMI.
and 3BDD011934-600_A_en_System_800xA_6.0_Device_Management_PROFIBUS_and_HART_Config
uration.
To install HART functionality select "Device Management PROFIBUS and HART" in system configuration console.
HART Information can be displayed only in a DTM and not in HMI if HART device is connected to S800 I/O.
With S900 I/O you can display secondary HART variables in HMI.