Where can I see the overcurrent protection setting?
ACS880-07-1160-7
20.03 Maximum current 796A
I can't find Overcurrent protection setting.
There is 1.65....3.5*Imax in the manual.
Thanks.
20.03 Maximum current 796A
I can't find Overcurrent protection setting.
There is 1.65....3.5*Imax in the manual.
Thanks.
Voted best answer
Hi,
As per FW manual, for ACS880 the general current settings are stored in:
99.06 Motor Nominal Current (from the nameplate) "The allowable range is 1/6…2 × IHd of the drive"
30.17 Maximum Current of the motor
As per FW manual, for ACS880 the general current settings are stored in:
99.06 Motor Nominal Current (from the nameplate) "The allowable range is 1/6…2 × IHd of the drive"
30.17 Maximum Current of the motor
Source: 3AUA0000085967 Rev C