800xA HI - Confirmed write support
Hi!
I have added a SignalReal in my SIL application.
The value should be manoeuvrable from the 800xA Workstation.
The icon/faceplate is available in the HMI, but the access is denied to the object.
I don't know which aspect to change to enable the object.
I read in the manual that I should use the "Confirme write Support" aspect. But I don't understand what settings to change to enable the object.
I have the right permission since I am able to manoeuvre already existing objects of the same type.
Does anyone have any idea for the proper settings/solution?
Best regards Conny
Voted best answer
You need to use aspect Application at object application, select your block and change Access type
Answers
Problem solved!
I found the place where the settings are made, under the Safaty application/Diagram/SIL folder.
//Conny
I found the place where the settings are made, under the Safaty application/Diagram/SIL folder.
//Conny