800 xA system HI Alarm delete
Hello,
I worked with 800xA and tried to delete a high alarm and make it (no alarm/only event) .... i opened the control module connection and it was read only even when i take over the reservation for its application only so please advice on following:
1- should I takeover the whole project if it reserved by another user or the only needed application is enough?
2- how can i change the parameter (i.e. make CM read/write and change the parameter)? and can it be done from both engineering work station and CBM?
3- if i have internal set point of level soft controller LIC can be accesses from faceplate, how can i modify the set point from Logic? as i cannot find set point in CM editor or in CM connection
THANKS
I worked with 800xA and tried to delete a high alarm and make it (no alarm/only event) .... i opened the control module connection and it was read only even when i take over the reservation for its application only so please advice on following:
1- should I takeover the whole project if it reserved by another user or the only needed application is enough?
2- how can i change the parameter (i.e. make CM read/write and change the parameter)? and can it be done from both engineering work station and CBM?
3- if i have internal set point of level soft controller LIC can be accesses from faceplate, how can i modify the set point from Logic? as i cannot find set point in CM editor or in CM connection
THANKS
Answers
hi,
1.It is enough to reserve the application which is required to change,if you have any chance to change the global variables in project level then it is required to reserve the whole one.
2.For changing any parameter of control module it can be done from Engineering station CBM.
3.If u have access to change the setpoint from faceplate then you can go ahead and change. or else if u need to change from the logic then it might availabe as a datatype from any parameter in the control module.
1.It is enough to reserve the application which is required to change,if you have any chance to change the global variables in project level then it is required to reserve the whole one.
2.For changing any parameter of control module it can be done from Engineering station CBM.
3.If u have access to change the setpoint from faceplate then you can go ahead and change. or else if u need to change from the logic then it might availabe as a datatype from any parameter in the control module.
by yasir.rashid Rank: 827 on 11/23/2020 1:25:35 PM | Like (0) | Report
thanks a lot.