firmware Update
Hey Experts
I have a problem with ABB ACS480 Drive , some of them not all
its that some parameter missing , fro example if i need to change the source of the frequency reference (To potentiometer) we need to get access to parameter 28.11 and change number (18>> keypad) to number (1 >> potentiometer) so some acs480 when i get access to 28.11 dose not have the number 1 , its only have (0,4,5,8,18,20) so (1 ) is missing , i wonder what am missing and how can we update the firmware for ACS480 ?
I have a problem with ABB ACS480 Drive , some of them not all
its that some parameter missing , fro example if i need to change the source of the frequency reference (To potentiometer) we need to get access to parameter 28.11 and change number (18>> keypad) to number (1 >> potentiometer) so some acs480 when i get access to 28.11 dose not have the number 1 , its only have (0,4,5,8,18,20) so (1 ) is missing , i wonder what am missing and how can we update the firmware for ACS480 ?
Answers
Hi
Some parameters can be directly obscured by the drive, depending on how it is programmed.
First you should always indicate in your questions what model / size of drive you are talking about, then what motor the drive is used for and finally what the application is.
If you can post the parameters file, maybe we can help you, as you described your problem, I don't think.
As for the FW, it is not an operation allowed to std users. You must contact your nearest ABB dealer and ask if the tool for updating the FW is needed by means of the Service.
In any case, the FW update file is only granted to service technicians and cannot be released to end users.
BR
Flavio
Some parameters can be directly obscured by the drive, depending on how it is programmed.
First you should always indicate in your questions what model / size of drive you are talking about, then what motor the drive is used for and finally what the application is.
If you can post the parameters file, maybe we can help you, as you described your problem, I don't think.
As for the FW, it is not an operation allowed to std users. You must contact your nearest ABB dealer and ask if the tool for updating the FW is needed by means of the Service.
In any case, the FW update file is only granted to service technicians and cannot be released to end users.
BR
Flavio
Hi,
I believe that you don't need to reload the firmware - for the machinery drives I don't know variants of the standard firmware.
For ACS480: if the parameter 28.11 gives only 0,4,5,8... most probably you have activated Fieldbus control for the drive. That's why the other options are hidden.
Check the corresponding parameters, e.g. 20, 22 where control is given to FB...
I believe that you don't need to reload the firmware - for the machinery drives I don't know variants of the standard firmware.
For ACS480: if the parameter 28.11 gives only 0,4,5,8... most probably you have activated Fieldbus control for the drive. That's why the other options are hidden.
Check the corresponding parameters, e.g. 20, 22 where control is given to FB...
Source: ACS480 FW manual
Add new comment