Can AIC's be created in an 800M. ( I normally work with the AC450) I need to create calculated values in the 800M and send them to my 800xA system Control Structure so I can display them on operator screens.
Thanks
Thanks
Answers
Depends on the library used. Pulp and paper library has a one to one function block, called AIC01. Don't know what might be available in other libraries.
Peter
The "Pulp & Paper Library" is an attempt to make an AC800M appear identical to an AC450 from an operators point of view. ( Internally, the library is quite different from AC450 )
Its not perfect, but its pretty close. Most likely if you are expanding or replacing an Advant Master based system you would have been offered this library as part of the upgrade. The Library contains matching functions for all of the Advant object types. Including AIC.
If you don't have this library, you can buy it, or build something similar to an AIC element using the standard Control Builder Libraries and display components.
Its not perfect, but its pretty close. Most likely if you are expanding or replacing an Advant Master based system you would have been offered this library as part of the upgrade. The Library contains matching functions for all of the Advant object types. Including AIC.
If you don't have this library, you can buy it, or build something similar to an AIC element using the standard Control Builder Libraries and display components.
Hi,
You can use the SignalRealCalcInM from SignalLib which is equivalent to AIC block.