We have SYSTEM 800 xA v6.0.1 and some ABB REM620 Relays
We need to connect relays with control system by IEC61850 we have done configuration everything is ok but analoge variables such as voltage and current does not update in hmi as long as you change the page in hmi but digital variables like circuit breaker position is ok and update automatically without problem
Please help us to solve the problem
We have SYSTEM 800 xA v6.0.1 and some ABB REM620 Relays
We need to connect relays with control system by IEC61850 we have done configuration everything is ok but analoge variables such as voltage and current does not update in hmi as long as you change the page in hmi but digital variables like circuit breaker position is ok and update automatically without problem
Please help us to solve the problem
Answers
Hi,
All these points are configured in RCB?
Regards
ATP
All these points are configured in RCB?
Regards
ATP
Couple of points
1. Voltage and Current Logical Nodes are added in dataset?, respective dataset is linked to RCB? and ensure client mapping as well
2. Check deadband settings too
1. Voltage and Current Logical Nodes are added in dataset?, respective dataset is linked to RCB? and ensure client mapping as well
2. Check deadband settings too