freelance Graphics DigiVis faceplate warning
Dir sir
good morning
1- I add some motor controllers to the project and load it to the program but when I open the faceplate its give me a warning as the photo next, after that I load the program by whole station and the problem solve but when I make some modification and load again the problem came back, so please can you explain to me what I can do for this a matter.
thank you so much
best regards
good morning
1- I add some motor controllers to the project and load it to the program but when I open the faceplate its give me a warning as the photo next, after that I load the program by whole station and the problem solve but when I make some modification and load again the problem came back, so please can you explain to me what I can do for this a matter.
thank you so much
best regards
Answers
The Sign in the Faceplate signals "Local Operation".
Check your IDF for the Signal on LOC input.
Local Operation ist the highest Priority an the IDF will follow the FeedBack Signal with his Output.
Check your IDF for the Signal on LOC input.
Local Operation ist the highest Priority an the IDF will follow the FeedBack Signal with his Output.
by Dieter Henkel
Have a look at the Alarms coming from that function block. That could help in finding the reason.
by almohayak Rank: 669 on 10/19/2020 4:31:14 AM | Like (0) | Report
every thigs is normal
FLT=0
LOC=0
PR0=0
IN=1
FB1=1 (AFTER FEEDBACK COME)