Process Alarm not showing in alarm list
Hi im have up my system with actual controller and its module at site.
but 800xA process alarm did not show when i try to trigger an alarmcond FBD. All ABB services is running.I did test using soft controller to trigger alarm, it happend to show up. But in actual implementation on controller have such issue. Any advice or solution?


but 800xA process alarm did not show when i try to trigger an alarmcond FBD. All ABB services is running.I did test using soft controller to trigger alarm, it happend to show up. But in actual implementation on controller have such issue. Any advice or solution?


Voted best answer
CondState 5 should result in an alarm in the HMI.
- Is this particular controller connected on MMS A&E to the AC 800M OPC server?
- Is this connection having Subscription State 1 and having 0 (zero) Events to send?
(verify using Control Builder M > Application > Diagrams > Diagram 3 > SystemDiagnostics > Advanced > Alarm & Event > Subscriber 1 + 2)? - Is there an Event Collector service group and provider configured for this AC 800M OPC AE server?
- Is the alarm list filter including the Process Condition Event category?
Answers
Hi Stefan Stromqvist, thank for your comment.
Is this particular controller connected on MMS A&E to the AC 800M OPC server? Not quite understand of your question but the controller did connect to OPC Server Is this connection having Subscription State 1 and having 0 (zero) Events to send? (verify using Control Builder M > Application > Diagrams > Diagram 3 > SystemDiagnostics > Advanced > Alarm & Event > Subscriber 1 + 2)? refer photo 1, cant find diagram>diagram3.. under application Is there an Event Collector service group and provider configured for this AC 800M OPC AE server?Refer 2nd photo is this consider have or dont have? Is the alarm list filter including the Process Condition Event category?Refer 2nd photo that default did filter include process alarm only.



Is this particular controller connected on MMS A&E to the AC 800M OPC server? Not quite understand of your question but the controller did connect to OPC Server Is this connection having Subscription State 1 and having 0 (zero) Events to send? (verify using Control Builder M > Application > Diagrams > Diagram 3 > SystemDiagnostics > Advanced > Alarm & Event > Subscriber 1 + 2)? refer photo 1, cant find diagram>diagram3.. under application Is there an Event Collector service group and provider configured for this AC 800M OPC AE server?Refer 2nd photo is this consider have or dont have? Is the alarm list filter including the Process Condition Event category?Refer 2nd photo that default did filter include process alarm only.