IIT800xa HMI Alarm Not Matching With DI Object
I just completed MB300 upload (since we're adding new signal), but somehow, when we test the alarm for the new added signal, it doesn't shows according to the object name, and no description, and got "(1:1)". Refer attached for reference
Answers
The (x:y) suffix is a giveaway telling you that the alarm is associated in [Control Structure]/Lost & Found.
If an alarm or event trigger before MB300 Upload, the Event Collector service will fail to look up the object and fall back to create a temporary placeholder object below Lost and Found having the object name + a suffix (MB300 network decade:MB300 node number), e.g. (2:61) for MB300 network 21 controller node 61. Such alarms will have a very short context menu because the object type is not known.
Please read this post I made some days ago.
1. Monitor L&F while engineering (and later...)
2. Perform MB300 Upload if new L&F objects appear
3. Purge L&F
4. Trigger a new alarm or event
If an alarm or event trigger before MB300 Upload, the Event Collector service will fail to look up the object and fall back to create a temporary placeholder object below Lost and Found having the object name + a suffix (MB300 network decade:MB300 node number), e.g. (2:61) for MB300 network 21 controller node 61. Such alarms will have a very short context menu because the object type is not known.
Please read this post I made some days ago.
1. Monitor L&F while engineering (and later...)
2. Perform MB300 Upload if new L&F objects appear
3. Purge L&F
4. Trigger a new alarm or event
Add new comment