Display builder S+ engineering 2.2 issue
I have installed operation developer combined with SPE 2.2 in same workstation
I have 2 questions
1- in display builder , add to system not active , so what is missing ?
2- what is right sequence to upgrade the displays from PGP to existing version , if this a way to upgrade all displays in same time ?
Thanks
I have 2 questions
1- in display builder , add to system not active , so what is missing ?
2- what is right sequence to upgrade the displays from PGP to existing version , if this a way to upgrade all displays in same time ?
Thanks
Answers
Hi,
1. Check Engineering Server Name is properly configured under ClinetServer registry setting.
2. Place all the files in the work folder and execute the Updatedisplay.exe from SPO-> bin folder or just invoke one of the graphic and Add Multiple files to System option from the drop-down in the menu bar of display builder and select the folder.
Regards,
Farooq
1. Check Engineering Server Name is properly configured under ClinetServer registry setting.
2. Place all the files in the work folder and execute the Updatedisplay.exe from SPO-> bin folder or just invoke one of the graphic and Add Multiple files to System option from the drop-down in the menu bar of display builder and select the folder.
Regards,
Farooq