Alarm & Event List Configuration Aspect
Hi!
I have set up a new xA system version 6.1.
Sudddenly after a few weeks I've noticed very long response times when working with any Alarm & Event List Configuration Aspect.
Any ideas?
I activated Audit trail about the same time this problem occured so I deactivated Audit trail but no improvement.
I've restarted the Aspect servers as well as the Connectivity servers.
BRs Anders
I have set up a new xA system version 6.1.
Sudddenly after a few weeks I've noticed very long response times when working with any Alarm & Event List Configuration Aspect.
Any ideas?
I activated Audit trail about the same time this problem occured so I deactivated Audit trail but no improvement.
I've restarted the Aspect servers as well as the Connectivity servers.
BRs Anders
Voted best answer
Potentially a known problem - see Product Issue 800xASYS-OL-6100-10078 mentioned in product alert 2PAA119837 on ABB Library.
Solution: upgrade to ABB 800xA Base 6.1.0-0 Rollup 1, also published on ABB Library, 2PAA119842.
Please speak with your regional ABB sales representative if you lack access to ABB Library.
Solution: upgrade to ABB 800xA Base 6.1.0-0 Rollup 1, also published on ABB Library, 2PAA119842.
Please speak with your regional ABB sales representative if you lack access to ABB Library.
Answers
It sounds for me like a runtime filter is applied in the Alarm list. As the size of history database grows , so the alarm list filtering gets gradually longer.
That issue can be minimized if the filter is applied with defined shorter time interval (1 day, 1 week , etc)
That issue can be minimized if the filter is applied with defined shorter time interval (1 day, 1 week , etc)