communication error with IEC60870-5-104 Slave and Symphony Plus History 3.1 snanner
Our custommer has an old PGIM server 5.1 with IEC60870-5-104 slaves.
These slave's work fine in this version.
Now we are upgrading to SPlus history version 3.1.
We have no communication with the slaves.
I've tested the old DLL but this give's the same result.
I can communicate form the scanner system to the slave with a small program (QTester).
then i can se entry's in the wireshark.
When i start the scanmanager there is no entry in the wireshark.
In the log file i get these entry's
14.09.2020 19:06:46:590 (2148) CIPDevice::dumpConnection::"MPN480" local 0.0.0.0:59633 remote: 85.88.111.201:2404 14.09.2020 19:06:46:590 (2148) CTCPDevice::Connect:"MPN480" ConnectEx failed: 0 14.09.2020 19:06:46:590 (2148) CRTUDevice::onDisconnect:"MPN480" 14.09.2020 19:06:47:596 (2148) CRouter::AttachDevice:
I'm not sure at the Local 0.0.0.0 adres i think there is the problem But I don' know how to cange it or where to configure it.
Is there someone who has or had the same issues?
These slave's work fine in this version.
Now we are upgrading to SPlus history version 3.1.
We have no communication with the slaves.
I've tested the old DLL but this give's the same result.
I can communicate form the scanner system to the slave with a small program (QTester).
then i can se entry's in the wireshark.
When i start the scanmanager there is no entry in the wireshark.
In the log file i get these entry's
14.09.2020 19:06:46:590 (2148) CIPDevice::dumpConnection::"MPN480" local 0.0.0.0:59633 remote: 85.88.111.201:2404 14.09.2020 19:06:46:590 (2148) CTCPDevice::Connect:"MPN480" ConnectEx failed: 0 14.09.2020 19:06:46:590 (2148) CRTUDevice::onDisconnect:"MPN480" 14.09.2020 19:06:47:596 (2148) CRouter::AttachDevice:
I'm not sure at the Local 0.0.0.0 adres i think there is the problem But I don' know how to cange it or where to configure it.
Is there someone who has or had the same issues?
Answers
Hi,
Please check whether you have updated the following file: Ini file path : C:\Windows\Konfi_IEC60870_5_Scanner and windows Host file updation Content of IEC60870_5_Scanner.ini: #Sectionname like Hostname [GATEWAY02] ...
(other settings as well, if required)
Windows Hosts file:
192.168.1.xx GATEWAY02
For more info, refer to 7.18 IEC60870-5-104 section of 2VAA007009-310_A_en_Splus_Historian_3.1_Installation_and_Administration_user_ma
nual
Regards,
Farooq
Please check whether you have updated the following file: Ini file path : C:\Windows\Konfi_IEC60870_5_Scanner and windows Host file updation Content of IEC60870_5_Scanner.ini: #Sectionname like Hostname [GATEWAY02] ...
(other settings as well, if required)
Windows Hosts file:
192.168.1.xx GATEWAY02
For more info, refer to 7.18 IEC60870-5-104 section of 2VAA007009-310_A_en_Splus_Historian_3.1_Installation_and_Administration_user_ma
nual
Regards,
Farooq