Is Pre-Trip Limit feature available for 800xa SIS programming?
I have configured two Trip Alarms let's say Low Low at 20.0 and High High at 90.0 for Transmitter. Now I want to configure Pre-Trip Operator Alerts at 10.0 for LL and 80.0 for HH or Pre-Trip Alert with respect to percentage e.g. 5% value of the HH/LL Set point?
So is this kind of feature available for SIS programming in 800xa?
So is this kind of feature available for SIS programming in 800xa?
Answers
An optional HL (high/low) pre-alarm can be generated to warn the operator of an impending trip . This is also depends on the library you are using as well.