AC900F freelance 2013
Dear sir
Good evening
I use ABB freelance 2013 and I have some question as next:
1- Sometimes I need to make some modification in the program and upon downloading the following message appears: (Resource will be stopped for download). Then all motors stop, and sometimes this message does not appear and the download is completed without anything stopping.
The question: What are the reasons for this message appearing?
2- I make bag counter use Proximity sensor connect it to the digital input in IOP and puls counter (CT_P)in FBD according to the picture, companionship, but the reading in the monitor is not correct (is less than actual) some puls the counter not count it.
3- Howe I can add new OS to the system
Thank you so much
best regards
Answers
1. Stop the resource or download while full run depends on the kind of changes you made.
2. Counting impulses by simple digital input only works if the program cycle time is always shorter than the low time and also the high time. If not, some impulses are not counted.
To fix this you can decrease the cycle time or use a special counter input.
3. Which OS and which system?
Without this information I would start with: Place the installation DVD in the drive and restart.
Add new comment