800xA Client installation error

During Deploying from server to client i am getting this error posted here....
Please suggest what could be the cause.
i am using 800xA 6.1.0 with server 2016 OS
Client side : WINDOWS 10 ENT 2016 LTSB
Answers
Hello,
Check all pre-requisite met like HW/OS compatibility, required W patches, 3rd party sw, etc...
Based on image seems like client node not able to connect to Pri AS/CS, looks like network issue...
Check that all the nodes network cards set as per manual,
found on open Internet manual for network, https://library.e.abb.com/public/9c8b6c0dc8bdfe16c1257b400026feb3/3BSE034463-51
0_E_en_System_800xA_5.1_Network_Configuration.pdf, Page 132 onwards...
setting up network properly should resolve issue...
Else In ABB Lib look for getting started manual 2PAA111708-610, should help
Hope that helps....
Check all pre-requisite met like HW/OS compatibility, required W patches, 3rd party sw, etc...
Based on image seems like client node not able to connect to Pri AS/CS, looks like network issue...
Check that all the nodes network cards set as per manual,
found on open Internet manual for network, https://library.e.abb.com/public/9c8b6c0dc8bdfe16c1257b400026feb3/3BSE034463-51
0_E_en_System_800xA_5.1_Network_Configuration.pdf, Page 132 onwards...
setting up network properly should resolve issue...
Else In ABB Lib look for getting started manual 2PAA111708-610, should help
Hope that helps....
When using Windows Workgroup it is utmost important that all user accounts and user groups are synchronized across all computers.
A wrong password or group membership may explain why the client cannot connect to the server. RNRP must also be enabled and operational (server need to see the client)
A wrong password or group membership may explain why the client cannot connect to the server. RNRP must also be enabled and operational (server need to see the client)