IEC61850 CET version 6.1. computer node management not presenting and not working
Dear All,
I am not able to use ABB IEC61850 CET Version 6.1 Computer Node - Management option.
The Update / Reload Configuration options of Manager tab are not working and presenting.
I installed SQL packets and reinstalled IEC 61850 CET and IEC 61850 OPC Server some times but no change.
What can be the issue?
Looking forward comments of some experts soon!
Regards
Answers
Hi,
Are you using Legacy method in IEC61850 connect?
From v6.1 onwards, you need to upload &/ update SCD only in 800xA Engineering Workplace Control Structure, if you are not using legacy. Alarm Event definition and mappings also can be done in Engineering Workplace itself.
Need not to open CET in v6.1, if you are not using legacy. Utility manager is an alternative for Online diagnostics functions. Many more differences are there between v6.1 and till v6.0. Refer IEC61850 manual in 800xA documentation.