Backup CPU Stopped ,the F light is flashing and After init, the CPU is normal. This issue is occasionally appear.
In my project, There are 4 pairs of PM866CPU and redundant configuration with BC820. Named CPU1,CPU2,CPU3,CPU4; Only CPU3 backup CPU stopped occasionally whether upper CPU or Lower CPU, at this moment in processor unit, the F light is flashing. After press init button, The backup CPU is normal and P,B,Dual lights are on. Please see the log files and topology.
Voted best answer
Hi,
Here are some information i would like to highlight from the controller logs,
1. Your IAC communication is not stable?, there are some repetitive connection ups and downs in IAC MMS
I 2020-08-18 16:25:53.573 IAC: Connection up (IP = AC105098)
W 2020-08-18 16:26:22.935 IAC: Connection down (IP = AC105098)
2. IAC communication variable timeout as well
E 2020-08-18 16:26:22.934 On Unit= 0.5.1 HWError Ctrl_VMS3 0000 See HWTree Error 16#60020000 16#00000020
3. There are some problem in CI card-1 - Profibus communication failure between Primary and Backup
E 2020-08-18 16:37:51.131 Unit= 1.4 Ctrl_VMS3 0000 See HWTree Error 16#02020000 16#40000000
4. Backup (Lower) CPU stopped first due to some RCU error. Not sure whether it is by manual or auto?
E 2020-08-18 16:41:26.762 Unit= _SWTargets Ctrl_VMS3 4004 P:BkpNotAlive in Synch
E 2020-08-18 16:41:26.761 Unit= _SWTargets Ctrl_VMS3 4020 B:Bkp RCUError 08
E 2020-08-18 16:41:26.761 Unit= _SWTargets Ctrl_VMS3 4024 B:Backup CPU halted
5. Am not sure what is this below bus error?, someone can enlight me on this
E 2020-08-18 17:19:48.466 AnyBusDevMgr BUSERROR at module 3 address 401c02c0
6. Finally, the controller shutdown
E 2020-08-18 17:19:48.497 ErrorHandler PM: 4112 Hang CEX IRQ The upper PM has been shut down (1,4,ER)
E 2020-08-18 17:19:48.497 Error message PM: 4112 Hang CEX IRQ The upper PM has been shut down
E 2020-08-18 17:19:48.500 FATAL ERROR in ..\..\source\BASICS~1/ErrorHandler/errorhandler/errorhandlerimp.cpp[1625]: 872939520 (0x34080000)
F 2020-08-18 17:19:49.563 (local time) System Breakdown Walkback trigged by exception vector : 0x1000
It points out so many issues, but could not able to conclude on what exact scenario it leads to shutdown. Network issue is an another angle to look into this issue.
Anyway Pls register a supportline case with ABB to get a official support on this.
Here are some information i would like to highlight from the controller logs,
1. Your IAC communication is not stable?, there are some repetitive connection ups and downs in IAC MMS
I 2020-08-18 16:25:53.573 IAC: Connection up (IP = AC105098)
W 2020-08-18 16:26:22.935 IAC: Connection down (IP = AC105098)
2. IAC communication variable timeout as well
E 2020-08-18 16:26:22.934 On Unit= 0.5.1 HWError Ctrl_VMS3 0000 See HWTree Error 16#60020000 16#00000020
3. There are some problem in CI card-1 - Profibus communication failure between Primary and Backup
E 2020-08-18 16:37:51.131 Unit= 1.4 Ctrl_VMS3 0000 See HWTree Error 16#02020000 16#40000000
4. Backup (Lower) CPU stopped first due to some RCU error. Not sure whether it is by manual or auto?
E 2020-08-18 16:41:26.762 Unit= _SWTargets Ctrl_VMS3 4004 P:BkpNotAlive in Synch
E 2020-08-18 16:41:26.761 Unit= _SWTargets Ctrl_VMS3 4020 B:Bkp RCUError 08
E 2020-08-18 16:41:26.761 Unit= _SWTargets Ctrl_VMS3 4024 B:Backup CPU halted
5. Am not sure what is this below bus error?, someone can enlight me on this
E 2020-08-18 17:19:48.466 AnyBusDevMgr BUSERROR at module 3 address 401c02c0
6. Finally, the controller shutdown
E 2020-08-18 17:19:48.497 ErrorHandler PM: 4112 Hang CEX IRQ The upper PM has been shut down (1,4,ER)
E 2020-08-18 17:19:48.497 Error message PM: 4112 Hang CEX IRQ The upper PM has been shut down
E 2020-08-18 17:19:48.500 FATAL ERROR in ..\..\source\BASICS~1/ErrorHandler/errorhandler/errorhandlerimp.cpp[1625]: 872939520 (0x34080000)
F 2020-08-18 17:19:49.563 (local time) System Breakdown Walkback trigged by exception vector : 0x1000
It points out so many issues, but could not able to conclude on what exact scenario it leads to shutdown. Network issue is an another angle to look into this issue.
Anyway Pls register a supportline case with ABB to get a official support on this.
by ParthibanT Rank: 42 on 9/2/2020 3:17:33 AM | Like (0) | Report
CPU3 controller IP? Becoz so many controller logs are attached.
by lu-heng.li Rank: 807 on 9/2/2020 4:11:07 AM | Like (0) | Report
Sorry,CPU3 Controller IP :172.16.80.153,172.17.80.153 and 172.16.82.153,172.17.82.153;