Problem in commissioning with AC800FR
Hello there ; I have problem that effect to prevent download whole station to cpu (AC800FR) I replaced the FI 830 with another same because that caused past error in IP with error 21000023 and when i replace it now new message is appear (wrong station type)then when I (off all and on power)the new message (incompatible DMS version )so what can I do with this recent case and how can I solve the previous error caused by original FI830 F THAT CAUSED IP ERROR .
BEST WISHES ...
BEST WISHES ...
Voted best answer
FI830 is the Profibus DP module, right? Seems you have to flash the correct firmware version to this module.
If you replace the AC800F main unit, you have to flash the controller firmware too.
1. Start-->...-->Freelance-->Configure
If you want to flash the controller:
2. "Controller-Firmware-Update"
3. enter both IP's (you call it ac800f-R-, so I assume it's a redundant one)
4. double check the IP's (you don't want flash the wrong station!)
5. "load"
6. wait until the controllers are up again
If you want to flash the Profibus Modules
7. "Profibus-Modul Firmware-Update"
7. enter both IP's
8. double check the IP's
9. "load"
10. wait. Should be much faster than the controller one.
After this you should be able to "load whole station"
If you replace the AC800F main unit, you have to flash the controller firmware too.
1. Start-->...-->Freelance-->Configure
If you want to flash the controller:
2. "Controller-Firmware-Update"
3. enter both IP's (you call it ac800f-R-, so I assume it's a redundant one)
4. double check the IP's (you don't want flash the wrong station!)
5. "load"
6. wait until the controllers are up again
If you want to flash the Profibus Modules
7. "Profibus-Modul Firmware-Update"
7. enter both IP's
8. double check the IP's
9. "load"
10. wait. Should be much faster than the controller one.
After this you should be able to "load whole station"
Answers
To bypass the loading of the entire station, you work best with a reserve CPU.
Insert the Profibus card to be initialised into a reserve CPU and run the flashing of the firmware there.
Then the FI830 card can be used easily in the target controller.
Make sure that you are using the right CBF version for flushing.
Best way you are using origin CBF station connected only to your reserve CPU to avoid loading wrong station.
Regards
T.R.
Insert the Profibus card to be initialised into a reserve CPU and run the flashing of the firmware there.
Then the FI830 card can be used easily in the target controller.
Make sure that you are using the right CBF version for flushing.
Best way you are using origin CBF station connected only to your reserve CPU to avoid loading wrong station.
Regards
T.R.