800XA: AC800M Engineering station on control network
800XA 6.1 with NE870 RNRP router .
Is it possible to deploy an Engineering client which connected only to control network (AC800M) ?
Is it possible to deploy an Engineering client which connected only to control network (AC800M) ?
Answers
This question has not yet been answered.
by David Greening Rank: 204 on 8/27/2020 12:19:38 AM | Like (0) | Report
Some thoughts...
If you are in a Domain - is your Domain available on the control network - you will need your security credentials.
How will you open Aspects/Code etc - Is the Aspect system on the control network?
by backdraft
The RNRP Router is connecting the networks so you can open "all" ports to allow connecting clients behind the firewall, assuming all Servers are using RNRP, but not sure why to install the router at all in this configuration...
by
Not tested.
Joining and staying member of the domain on the non-domain network must work or else 800xA won’t work.
RNRP can be routed with NE870 or regular connectivity server. Likely not an issue here.
You may try this but be prepared to fall back on proven configurations.
by RPM Rank: 37 on 8/29/2020 7:48:39 AM | Like (0) | Report
Due to any specific limitation ABB has restricted this option ?
by
Testing resources are limited; not all possible permutations can be tested.