How to unblock port disabled due to network loop detection in the AC800M 5.1 version
How to unblock port disabled due to network loop detection in the AC800M 5.1 version.
Previous month there was Network loop issue and we figured out that this was due to the one of the faulty network switch and the issue was fixed, but due to some reason some of the controller ports ( CN1) is still disabled due to this network loop and its showing the old date when the incident happened last onth.
Previous month there was Network loop issue and we figured out that this was due to the one of the faulty network switch and the issue was fixed, but due to some reason some of the controller ports ( CN1) is still disabled due to this network loop and its showing the old date when the incident happened last onth.
Answers
Before firmware version 5.1.1-3 a bug may keep ports blocked following a dual storm until the controller is reset.
A workaround in this state (if controller is pingable) is to download a dummy RNRP parameter change, eg Max No Of Remote Areas which will restart RNRP which should unblock the port.
A workaround in this state (if controller is pingable) is to download a dummy RNRP parameter change, eg Max No Of Remote Areas which will restart RNRP which should unblock the port.