"connection down" displayed in gateway under CI867 module.
CI867 as master, Has already established connection with a RTU slave via gateway Moxa MB3480, But RS-485 cable is pulled out on the slave end, the slave unit is error marked in Project Explorer. How to reestablished the communication and Clear the error in project Explorer.
Please see the pic.
Please see the pic.
Voted best answer
Hi,
The Picture is not attached.
Connect back the RS-485 cable at the Slave side (2 wire Data+, Data-, GND or 4 wire Tx+, Tx-, Rx+, Rx-, GND shall be connected as recommended), the communication should resume back on it's own.
You can use Clear Latched Unit Status in System Status Viewer or CBM to clear the latched errors.
The Picture is not attached.
Connect back the RS-485 cable at the Slave side (2 wire Data+, Data-, GND or 4 wire Tx+, Tx-, Rx+, Rx-, GND shall be connected as recommended), the communication should resume back on it's own.
You can use Clear Latched Unit Status in System Status Viewer or CBM to clear the latched errors.