RTU540 TCP/IP SLAVE ID Change
Hi
The scada program I'm using doesn't support 255 slave id. It needs to be between 1 and 31. I don't know how to change it
The scada program I'm using doesn't support 255 slave id. It needs to be between 1 and 31. I don't know how to change it
Answers
Hi,
AFAIK, it is not possible to change the unit ID of the RTU540 to any other value other than 255. Manufacturers of Gateways/Bridge devices usually set 0 or 255 as the unit ID for such devices, when the device itself is acting as a Modbus TCP/IP server. Values 1-247 are reserved for Modbus RTU slave devices connected to a gateway unit's RS485 port, if any.
Regards
Rahil
AFAIK, it is not possible to change the unit ID of the RTU540 to any other value other than 255. Manufacturers of Gateways/Bridge devices usually set 0 or 255 as the unit ID for such devices, when the device itself is acting as a Modbus TCP/IP server. Values 1-247 are reserved for Modbus RTU slave devices connected to a gateway unit's RS485 port, if any.
Regards
Rahil