Is it possible to connect one operator workplace into two different 800xA system.
Dear All,
We have two 800xa system for each block and dedicated operator workplaces for each block but now requirement is that one operator workplace should get both block data in plant network.How we can establish this requirement? how to add/Is it possible same client in both 800xA system in SCC?
below is the simple details of system architecture.
One Domain (Single Plant networks ,Two separate Control network)
Two 800xa system
Thank you.
We have two 800xa system for each block and dedicated operator workplaces for each block but now requirement is that one operator workplace should get both block data in plant network.How we can establish this requirement? how to add/Is it possible same client in both 800xA system in SCC?
below is the simple details of system architecture.
One Domain (Single Plant networks ,Two separate Control network)
Two 800xa system
Thank you.
Answers
Hi!
There are several similar Q/A in this forum if you google.
Simple answer: No you can't.
But I would recommend you to check out Multisystem Integration (3BSE037076-xxx manual), put a new 800xA system on top.
BR
There are several similar Q/A in this forum if you google.
Simple answer: No you can't.
But I would recommend you to check out Multisystem Integration (3BSE037076-xxx manual), put a new 800xA system on top.
BR