ACH 580 is not giving output voltage 415V / analog input is 10Vdc through BMS
I am using new ACH 580 drive on HVAC - AHU unit, through BMS Analog input is 10VDC Frequency 50hz but Voltage output is 230V, actually I need to run the motor on full speed 415V
VFD running on 50HZ through BMS but output voltage is not 415V
Drive input voltage - 415Vac
MAXIMUM FREQUENCY - 50HZ
23.11 - DI1
23.12 - 20.00 S
23.13 - 20.00 S
30.13 - 0.00 HZ
30.14 - 50 HZ
VFD running on 50HZ through BMS but output voltage is not 415V
Drive input voltage - 415Vac
MAXIMUM FREQUENCY - 50HZ
23.11 - DI1
23.12 - 20.00 S
23.13 - 20.00 S
30.13 - 0.00 HZ
30.14 - 50 HZ
Answers
Hi
how you configured the parameters of group 99 - motor data ?
The operation of the drive depends on how many parameters are set, let's start with those concerning the electric motor
BR
Flavio
how you configured the parameters of group 99 - motor data ?
The operation of the drive depends on how many parameters are set, let's start with those concerning the electric motor
BR
Flavio