ac800m set ip adress for two plcs operating in redundant mode.
Replacing a new PLC AC800M into it is a backup PLC, but I don't know how to set the address for the spare PLC. Allow the 2 sets of PLC to operate in redandunt mode.
Voted best answer
Basic rule: Check the thick cable that connects both CPUs. One end of the cable is marked "upper". CPU at this cable side is Primary. Opposite CPU is Backup.
Backup PLC doesn't need IP address configuration. IP addresses of both CPUs are defined in the Primary CPU. Backup CPU reads IP address from Primary after power on.
Backup PLC doesn't need IP address configuration. IP addresses of both CPUs are defined in the Primary CPU. Backup CPU reads IP address from Primary after power on.
Answers
Hi,
For IP Address setting for AC800M controller need to use IP config tool. with TK212 cable to be connected in COM4 port.
For Redundant controller no need to set the IP address enable the redundancy in primary controller thats it.
For IP Address setting for AC800M controller need to use IP config tool. with TK212 cable to be connected in COM4 port.
For Redundant controller no need to set the IP address enable the redundancy in primary controller thats it.
Add new comment