PM582 Showing Error.
ABB PM582 showing error E4 003, d1 014, d2 255, d3 002, d4 000.
Please help to get rid of this problem.
Please help to get rid of this problem.
Is there any way to find out the I/O?
When i try to download my backup program, it shows me following error in bottom of CodeSys.
#251596803: '-1970-01-01 00:06:11 E4:I/O-Bus 'Timeout while updating the I/O data at program start'
Hi
Exactly as the program shows you:
some of the I / O are not responding to communication with the CPU.
How many I / O do you have in your PLC?
Are there any false contacts / dust / humidity in the connections between the communication bases?
Have you tried cleaning the base connectors with contact spray?
The extended error code, based on the tables I sent you on the answer, should help you understand which module is not responding
Thank you, It worked after replacing one module with terminal base.
Very well, I am glad that my suggestion served to solve your problem