How to create an alarm if a backup fails?
Hello together,
is it possible to get an alarm if a backup was not successfully? Our System is 800xA V5.1 FP4. Which configuration has to be done in the system? Maybe there is a manual which describes the steps to be done.
Thanks for reply.
Stay healthy,
Stephan
is it possible to get an alarm if a backup was not successfully? Our System is 800xA V5.1 FP4. Which configuration has to be done in the system? Maybe there is a manual which describes the steps to be done.
Thanks for reply.
Stay healthy,
Stephan
Answers
do you need to chech it manually.
if your backup is failing you should check the system, because it is not good, probably there is a problem,
check the information related, and try to fix it.
because one bad backup does not serve orit is not good idea to use for restore if you have problems.
if your system is ok, the backup is normally ok.
if your backup is failing you should check the system, because it is not good, probably there is a problem,
check the information related, and try to fix it.
because one bad backup does not serve orit is not good idea to use for restore if you have problems.
if your system is ok, the backup is normally ok.
Don't really know... but, can you use the alarm expression aspect in the service structure?
I get a system event when a backup is started and when a backup is finished.
I have read in the docs that there is a system alarm if we are out of storage
I get a system event when a backup is started and when a backup is finished.
I have read in the docs that there is a system alarm if we are out of storage
Hi!
Check "3BSE036904-510_D_en_System_800xA_Operations_5.1" manual.
Appendix A lists the most important System Alarms including backup storage reaching max size limit (mentioned above).
You can use this to trigger an External Alarm or setup SMS or email notification (however the latter requires license).
BR
Check "3BSE036904-510_D_en_System_800xA_Operations_5.1" manual.
Appendix A lists the most important System Alarms including backup storage reaching max size limit (mentioned above).
You can use this to trigger an External Alarm or setup SMS or email notification (however the latter requires license).
BR