Dear All,
Can we run a motor designed for star connection with the help of ACS150 drive? This is 1.5Kw motor designed with star connection 400Vac, 960 rpm.
Regards,
SS
Can we run a motor designed for star connection with the help of ACS150 drive? This is 1.5Kw motor designed with star connection 400Vac, 960 rpm.
Regards,
SS
Answers
In general, for VFD it does not matter whether the motor is connected in star or delta connection. Voltage and current are significant. Compare VFD parameters of output voltage and output current that must be equal or higher than the motor voltage and amps for the star connection.