Hello,
We are suffering an unusual issue with the one of the ABB ACS880 Drives, it is stopping and We are getting NO fault in the Drives AOP but on the DCS side we are getting bus fault, i have checked the drive event manager with drive composer but no faults are there
by comparing the parameter of the Drive with other drives, we found that all other drives having "ABB drives" selected in parameter 51.05, while this drives is having "PROFIDrive" in the Parameter 51.05, is that is the problem?
We are suffering an unusual issue with the one of the ABB ACS880 Drives, it is stopping and We are getting NO fault in the Drives AOP but on the DCS side we are getting bus fault, i have checked the drive event manager with drive composer but no faults are there
by comparing the parameter of the Drive with other drives, we found that all other drives having "ABB drives" selected in parameter 51.05, while this drives is having "PROFIDrive" in the Parameter 51.05, is that is the problem?
Voted best answer
Hi
to help us better understand your problem, please always indicate the model of the drive and the type of fieldbus, as well as the type of controller (DCS or PLC) you are using.
Generally ProfiDRIVE is used in parameter 51.05 when the drive is working as ProfiBus slave, if you give us more information we can help you better.
You should also specify whether the problem occurred immediately, at the first start-up, or after some time after commissioning, and in this case, if following any changes made to the system.
BR
Flavio
to help us better understand your problem, please always indicate the model of the drive and the type of fieldbus, as well as the type of controller (DCS or PLC) you are using.
Generally ProfiDRIVE is used in parameter 51.05 when the drive is working as ProfiBus slave, if you give us more information we can help you better.
You should also specify whether the problem occurred immediately, at the first start-up, or after some time after commissioning, and in this case, if following any changes made to the system.