Compact Control Builder AC 800M 5.1.1 closes after Fatal call to ErrorHandler
Hello,
I wanted to connect to PLC and then this message occured "Fatal call to ErrorHandler, see the log for further information". After this error compact builder stopped working and I couldn't download the program to the controller.
Can someone please help me?
Thank you for your help.
Best regards
Tomas
I wanted to connect to PLC and then this message occured "Fatal call to ErrorHandler, see the log for further information". After this error compact builder stopped working and I couldn't download the program to the controller.
Can someone please help me?
Thank you for your help.
Best regards
Tomas
Answers
Hi,
From the Log:
I 2020-06-23 11:17:47.673 Download And Online: Analyse and Check downloadable items E 2020-06-23 11:17:47.845 E 2020-06-23 11:17:47.846 Assertion: The BuildVersion is out of scope, the code need to be uppdated
Some version mismatch it seems, check the Controller Type and Firmware Version between Controller and Control Builder configuration.
From the Log:
I 2020-06-23 11:17:47.673 Download And Online: Analyse and Check downloadable items E 2020-06-23 11:17:47.845 E 2020-06-23 11:17:47.846 Assertion: The BuildVersion is out of scope, the code need to be uppdated
Some version mismatch it seems, check the Controller Type and Firmware Version between Controller and Control Builder configuration.