I want to filter out all the Alarms with ‘RTN’ AlarmState and leave only ACT and blank AlarmState
I want to filter out all the Alarms with ‘RTN’ AlarmState and leave only ACT and blank AlarmState. Issue is that it filters out AlarmState = blank as well.
Answers
Right click on an event, select Event Details and compare event with ACT, RTN vs. "blank". You can see that the latter (Event Type: Condition Event vs. Simple Event) lacks event attribute "Alarm State". This is probably the reason of your problem, when a filter is set for a non-existing attribute, event is excluded from results.
You can work around this by adding Alarm State attribute to respective Alarm Collection Definition in Library Structure. Look for "Event Attributes Definitions" in 3BSE037410-600_B_en_System_800xA_6.0_Administration_and_Security.pdf.
You can work around this by adding Alarm State attribute to respective Alarm Collection Definition in Library Structure. Look for "Event Attributes Definitions" in 3BSE037410-600_B_en_System_800xA_6.0_Administration_and_Security.pdf.