"External Alarm Silence" only working for members in "IndustrialItAdmin"
As the title says, I cannot silence external alarms with a standard operator account using a hotkey.
If the account Is added to "Administrators" In SCC, the hotkey Is working fine.
No changes can be found In "Aspect system structure" for either "Hot Keys" or "External Alarm Silence"
Any suggestions?
System version 6.1.0.1
Answers
Proably a permission setting problem.
Is the hotkey verb writing "FALSE" to the OPC property driven by the External Alarm Configuration, or calling the Silence Verb on the External Alarm Silence aspect?
Check permission on the OPC property driven by the External Alarm. The only difference being member of the Administrators User Group in 800xA User Structure (which I assume you are hinting of) is that the members can bypass security.
In practise, using the External Alarm Silence verb is basically the same as writing "FALSE" on the OPC property.
Is the hotkey verb writing "FALSE" to the OPC property driven by the External Alarm Configuration, or calling the Silence Verb on the External Alarm Silence aspect?
Check permission on the OPC property driven by the External Alarm. The only difference being member of the Administrators User Group in 800xA User Structure (which I assume you are hinting of) is that the members can bypass security.
In practise, using the External Alarm Silence verb is basically the same as writing "FALSE" on the OPC property.