Compact HMI as OPC UA Client
Hi,
Does Compact HMI (CHMI 6+) Support OPC UA or it only support OPC DA?
If so, do i need additional license to connect to third party OPC UA Servers?
Regards,
Abdelrazzaq Hiasat
Does Compact HMI (CHMI 6+) Support OPC UA or it only support OPC DA?
If so, do i need additional license to connect to third party OPC UA Servers?
Regards,
Abdelrazzaq Hiasat
Voted best answer
I don't know what happened to the answer I posted some 7 hours ago - the status is "Answered by Stefan Stromqvist 7 hrs ago" but there is 0 answers listed?
Looks like AKS ate the answer?
My answer was: there exists no OPC UA support in any version of CHMI nor 800xA as of writing.
The upcoming 800xA 6.1.1 release is likely to address that lack. CHMI is typically slightly behind the 800xA release cycle.
Please speak with your regional ABB sales representative for more more details.
Looks like AKS ate the answer?
My answer was: there exists no OPC UA support in any version of CHMI nor 800xA as of writing.
The upcoming 800xA 6.1.1 release is likely to address that lack. CHMI is typically slightly behind the 800xA release cycle.
Please speak with your regional ABB sales representative for more more details.
Source: .
Answers
Neither CCB nor 800xA support OPC UA today.
There are rumours the upcoming 800xA 6.1.1 release will bring UA support...
800xA History has some UA support today; unclear how this historian can be used to interact with other OPC UA servers and clients.
There are rumours the upcoming 800xA 6.1.1 release will bring UA support...
800xA History has some UA support today; unclear how this historian can be used to interact with other OPC UA servers and clients.
Add new comment