acs880
i have the fault code 5080 on acs880-01-0430 i changed the 2 fan but the fault is again
Answers
Source: ACS880 FW MANUAL
Hi Flavio I can epxlain that the first i have problem with power module MCD312 that was broken 2 phase so 2 pcs i changed them and after i try to start the driver show me the fault code 5080. i thought are the cooling fan in the lower part of the driver so i taked the other 2 from another driver acs880 that i have in the factory and fixed in the first one driver but is the same fault
Hi
based on what you wrote to me more, I think the fault is in the control board, perhaps damaged by the first fault in the power unit.
I suggest you contact the ABB Service who can help to you solve the problem.
BR
Flavio
based on what you wrote to me more, I think the fault is in the control board, perhaps damaged by the first fault in the power unit.
I suggest you contact the ABB Service who can help to you solve the problem.
BR
Flavio