Value getting updated even with no connection to device in LDHSE
We are working on Freelance CBF 8.2 with LDHSE 1.40 V and 010005.cfh capability file.
LDHSE got initialised and H1 port got activated. But download not happening showing the error no connection to device even though it is available in the live list.
But values of the instruments in the first H1 trunk getting updated in their respective tag even though "no connection" message displays in the Hardware structure of the H1 port.
Remaining trunk instrument values are not getting updated.
I have attached screenshots explaining the same (for eg tag TT110). It shows no connection in hardware structure of all H1 port, no value in the FBAPP blocks, but value is getting updated in the tag as per value window.
I have confirmed that no write cross-reference to that tag other than IO editor which is of the FF.
LDHSE got initialised and H1 port got activated. But download not happening showing the error no connection to device even though it is available in the live list.
But values of the instruments in the first H1 trunk getting updated in their respective tag even though "no connection" message displays in the Hardware structure of the H1 port.
Remaining trunk instrument values are not getting updated.
I have attached screenshots explaining the same (for eg tag TT110). It shows no connection in hardware structure of all H1 port, no value in the FBAPP blocks, but value is getting updated in the tag as per value window.
I have confirmed that no write cross-reference to that tag other than IO editor which is of the FF.
Answers
Hello,
If there had been a successful download to the devices of the first link previously, the devices are configured to publish as necessary.
For receiving published data no client/server connection is required, only some session and VCR and scheduling (LAS) configuration in the LD.
Understanding the failing connections is a different issue.
Best regards
Jürgen
If there had been a successful download to the devices of the first link previously, the devices are configured to publish as necessary.
For receiving published data no client/server connection is required, only some session and VCR and scheduling (LAS) configuration in the LD.
Understanding the failing connections is a different issue.
Best regards
Jürgen
by kamz Rank: 2611 on 5/25/2020 3:40:19 AM | Like (0) | Report
Why this could be happening? what modification to be done to activate all H1 ports of the LDHSE?