Energy meter correct data reading problem from CI854
I am facing problem in reading correct data from Energy meter 6400em schnieder....
I am getting same real time energy data from energy meter to DCS from Anybus converter to convert modbus to profibus communication..
But may data is not continuesly increasing with the energy meter data.
energy data of DCS is increasing once in 24 hours and keep on fluatuating in the range of data....
any help to solve this problem is appreciated...
Answers
According to your description, 6400em is Modbus slave and you are using a Modbus-profibus coverter connect to CI854. We have done a lot with schnieder EMs using CI853 with modbus communication, which means the EM is probably all right. And the converter is from professional vendor it quality and function should be all right as well. As I know for CI854 connect 3rd party profibus device, you need to import a GSD file to get the data structure. And the converter should need a configuration to mapping modbus register to profibus data. So is there any chance that the mapping has some configuration error? As I experienced some of the vender provide the modbus device with address 0-based and some are 1-based, which may result a misordered data table.