Energy meter correct data reading problem from CI854
I am facing problem in reading correct data from Energy meter 6400em schnieder....
I am getting same real time energy data from energy meter to DCS from Anybus converter to convert modbus to profibus communication..
But may data is not continuesly increasing with the energy meter data.
energy data of DCS is increasing once in 24 hours and keep on fluatuating in the range of data....
any help to solve this problem is appreciated...
I am getting same real time energy data from energy meter to DCS from Anybus converter to convert modbus to profibus communication..
But may data is not continuesly increasing with the energy meter data.
energy data of DCS is increasing once in 24 hours and keep on fluatuating in the range of data....
any help to solve this problem is appreciated...
Answers
HI. I have worked with above configuration. 90% issue comes when you fetch the data in Anybus.
You have to check for correct register mapping. For cross checking your program, pay attention to LED5 of Anybus. If it blinks Green & in between red then you have issue with Anybus programming.
If LED5 continuously blinks green then it leaves you with the choice of selection of block to merge the higher & lower register addresses in control builder.
Try these 2 steps.
You have to check for correct register mapping. For cross checking your program, pay attention to LED5 of Anybus. If it blinks Green & in between red then you have issue with Anybus programming.
If LED5 continuously blinks green then it leaves you with the choice of selection of block to merge the higher & lower register addresses in control builder.
Try these 2 steps.
i am using DINTIO datatype in GSD hardware configuration for Energy meter and after that i am converting it to REALIO by block with factorising the value ...present problem is i am unable map the data coming from the energy meter,since the range parameters are not working properly for DINT data type....Any suggestion is appreciated...