AC900F trend
Dear Mr. Henkel, I have a question and hope to help me, how can I make the step of cursor small as much as at the trend? because in our system the step is a little bit wide. in the attached pictures, you can see the steps of the cursor and how I can't put the cursor in peak value. Your replay shall be highly appreciated.
Regards
Regards
Voted best answer
Answers
The points that can be selected depend on the sampling rate that you entered in the trend configuration.
In the trend picture you can have the "real data points" displayed.
The intermediate values are interpolated.
A jump only ever takes place between the saved data points
Your pictures refer to operation, you have to make the changes in the Control Builder.
In the trend definition.
Do you use the trend server or trend building blocks? With the trend building blocks, there is then the task in which they lie and the reduction gear is called. For example. Task cycle 1s, reduction 10 => a value in trend every 10s. With the trend server, the time is given in the definition. With standard settings, a maximum of one second value is possible here.