How to remove unnecessary alarm
Dear Colleagues
I hope everyone is well and safe during these critical times.
In our system, there is an air compressor working ON when pressure less than 15 bar and OFF (stop) when pressure more than 30 bar, this compressor controlled by FB IDF_1,
The question is when the compressor reached 30 it's stopped normal but always showing alarm as attached picture.
So, I want to remove this alarm because it’s really disturbing us.
Regards
Voted best answer
Hello,
there is no attachment but i think you are talking about an end position error of your IDF_1.
You can disable this message directly in FB block in commissioning mode (so you need now download)

disable the end position monitoring (by removing the hook)
User correction not write for permanent effect .
Hope that's your problem.
Regards
TR
there is no attachment but i think you are talking about an end position error of your IDF_1.
You can disable this message directly in FB block in commissioning mode (so you need now download)

disable the end position monitoring (by removing the hook)
User correction not write for permanent effect .
Hope that's your problem.
Regards
TR