ACS 355 PID SETTINGS FOR PRESSURE CONTROL
Hi Guys
I have failed to do the above.
I have set all 99 parameters.
I have used PID MARCO
I have a 4 to 20mA (0 -10 bar) pressure transducer. 2 wire sensor.
I have used AI1
I have set the ffg parameters
1001 = DI1
1003= 1
1103= AI1
1104= 0Hz
1105= 50Hz
1301= 20%
1302= 100%
4006= 22
4007=1
4008= 0Bar
4009= 10bar
4010=19
4011=5bar
4012=0bar
4013=5bar
4014=1
4016=1
4018=20%
4019=100%
I have failed to do the above.
I have set all 99 parameters.
I have used PID MARCO
I have a 4 to 20mA (0 -10 bar) pressure transducer. 2 wire sensor.
I have used AI1
I have set the ffg parameters
1001 = DI1
1003= 1
1103= AI1
1104= 0Hz
1105= 50Hz
1301= 20%
1302= 100%
4006= 22
4007=1
4008= 0Bar
4009= 10bar
4010=19
4011=5bar
4012=0bar
4013=5bar
4014=1
4016=1
4018=20%
4019=100%
- 4027=0
Answers
Hi
have you tried my APP at the follow link?
https://forum-controlsystems.abb.com/...
Hope this helps you
BR
Flavio
have you tried my APP at the follow link?
https://forum-controlsystems.abb.com/...
Hope this helps you
BR
Flavio
Add new comment