connection between Drive and PLC using D2D connection!
Hello everyone
Is it possible to make a connection between AC500(PM554) PLC and ACS800 drive using D2D connection on ACS800?
What is needed for this!?
Is it possible to make a connection between AC500(PM554) PLC and ACS800 drive using D2D connection on ACS800?
What is needed for this!?
Answers
Hi
the use of the D2D is generally used for specific applications between drives, for example master follower.
What you ask can be done using the same terminals on the drive side, but by configuring the connection as ModBus RTU, and in the same way on your PM554.
To get an idea of how this connection can be made, you can use my app as a trace regarding the connection between a drive and a CP600 panel
https://forum-controlsystems.abb.com/...
Hope this help you
BR
Flavio
the use of the D2D is generally used for specific applications between drives, for example master follower.
What you ask can be done using the same terminals on the drive side, but by configuring the connection as ModBus RTU, and in the same way on your PM554.
To get an idea of how this connection can be made, you can use my app as a trace regarding the connection between a drive and a CP600 panel
https://forum-controlsystems.abb.com/...
Hope this help you
BR
Flavio
by Milli Rank: 838 on 4/29/2020 3:55:49 AM | Like (0) | Report
excuse me, ACS800 is wrong! I mean ACS880 drive!