ACS 800-04 -0105-5 crane application not take start command from CDP or Joystick. NO fault show on Drive.
Change control card ,Power card but problem not solved.
Answers
Is this new installation or it was running before
Check group 16 for start enable and make sure to be "yes"
Check group 16 for start enable and make sure to be "yes"
Hi
I assume that you have already checked through the CDP panel the presence of the start signals in the parameter group 01.17 when you operate the joystick and the reference signal if it comes from an analog one, in parameter 01.18 or 01.19.
If you have already done these checks and from the connection diagram of the running consents, nothing is missing, a failure of the input card is possible but in this case, I suggest you contact the ABB service that will be able to help you better.
BR
Flavio
I assume that you have already checked through the CDP panel the presence of the start signals in the parameter group 01.17 when you operate the joystick and the reference signal if it comes from an analog one, in parameter 01.18 or 01.19.
If you have already done these checks and from the connection diagram of the running consents, nothing is missing, a failure of the input card is possible but in this case, I suggest you contact the ABB service that will be able to help you better.
BR
Flavio
Add new comment