Structure Text Programming Problem.
Voted best answer
Setting the IN1 and IN0 input only affects the outputs OU0 and OU1 in automatic mode.
If your block is also in local and that is how titus said for your program code, the block will adjust the output to the current end positions.
You have to change... ,LOC:= NOT(N7_XB),...
Answers
Greetings,
For Local Inpur of IDF_2, you need to invert in Structured Text side.
Hope it helps.
For Local Inpur of IDF_2, you need to invert in Structured Text side.
Hope it helps.