ACS880 Drive
Hi
Recently upgraded SAMI GS drive to ACS880 which I am not much familiar with. The application is really simple, used as soft starter and run at constant speed of 1150 rpm on centrifugal. So the required parameters configured on basic set-up, motor data etc. and requested ID Run. The ID Run completed in Standstill mode but gave fault FF61 auxiliary code 0000 0002. As per ABB manual the fault relates to speed and motor related parameters and that parameters looks alright.
I also tried run drive after ID run, it shows ampere but not rpm and motor doesn't run.
Any advise what could possibly wrong? Apologies if details are not enough, I will provide further
Thank you for your time to respond
Ash
Answers
Hi
first you should give more information on the type of electrical motor and drive ACS880 used - size, power in kW and even better if with a photo of the motor plate.
Then you could do a simple test of the V / F function, to understand if the drive is correctly controlling the motor.
After doing this test, you can do other checks before going to vector mode
BR
Flavio
first you should give more information on the type of electrical motor and drive ACS880 used - size, power in kW and even better if with a photo of the motor plate.
Then you could do a simple test of the V / F function, to understand if the drive is correctly controlling the motor.
After doing this test, you can do other checks before going to vector mode
BR
Flavio