HISTORIZAR ATOMOS DE TAG STATION S+
Hi Sebastian, how are you? I hope your things are fine. Live this world event COVID19 that I hope to overcome soon. I am writing to you regarding a query about historical S+ data. In the TAGS TYPE STATION we historicize the following ATOMS: ttt.PV (proces value), ttt.CO (control output) and ttt.SP (set point)... but, it´s possible to add, for the same TAG, that historizes the ttt.AUTO (it would be the atom that tells me if the station is in manual or automatic).
In the TAG, if I call "View Atoms", I see in the "History" column that the ttt.PV has an M (main) and ttt.CO and ttt.SP have an H (History) but I cannot modify it. I am sending you an attached screenshot. Thank you!!! See you!!!
In the TAG, if I call "View Atoms", I see in the "History" column that the ttt.PV has an M (main) and ttt.CO and ttt.SP have an H (History) but I cannot modify it. I am sending you an attached screenshot. Thank you!!! See you!!!
Voted best answer
Ciao Alberto, Modify the file that i show you in the image above, in both Operations Server, History = <DEFAULT> it's means use a registry parameter.
Enjoy.
Enjoy.
<a href="https://ibb.co/fvpcvKX"><img src="https://i.ibb.co/xHj4Hc2/Annotazione-2020-04-22-233858.jpg" alt="Annotazione-2020-04-22-233858" border="0"></a>
Answers
Hi:
Add this line in the ATOM this line => history="yes"/>
Put this atoms at the start.
Let me know if is work.
BR
Add this line in the ATOM this line => history="yes"/>
Put this atoms at the start.
Let me know if is work.
BR
Add new comment