3-Screen Navigation issue due to Tabbed Navigation
1) 3 screens are configured , tab navigation is provided in all 3 screens -> when click the tab navigation on 2nd and 3rd screen display open on the the first screen -> this is very much difficult for the operators as we are using EOW -X3
We are not facing any issue with Normal navigation -> its only with Tab navigation
2) Any object (Faceplate/Alarm) right click Context menu is opening on the 3rd screen right corner -> which make more difficult for operator to select alarm/trend aspect.
Can any one help to solve this issue.
We are not facing any issue with Normal navigation -> its only with Tab navigation
2) Any object (Faceplate/Alarm) right click Context menu is opening on the 3rd screen right corner -> which make more difficult for operator to select alarm/trend aspect.
Can any one help to solve this issue.
Answers
Hi,
Have you checked the number of screens, selected in Button Appearance tab of the workplace (page 122-123 of 3BSE030322-600_C, figure 99)
In your case it should be 3, respectively each tab will have 3 parts - for opening the graphic screen on each screen
Have you checked the number of screens, selected in Button Appearance tab of the workplace (page 122-123 of 3BSE030322-600_C, figure 99)
In your case it should be 3, respectively each tab will have 3 parts - for opening the graphic screen on each screen
Source: 3BSE030322-600_C
Add new comment