NTCL01 and NICL01
We have NICL01 in BAILEY infi90 system with IMMFP02 PCU. we have no spare NICL01, can we used NTCL01 in the replacement of NICL01.
Answers
The answer to your question is yes, technically you can intermix the NICL01 with the NTCL01 loop terminations. However, to replace an NICL01 Termination Module with an NTCL01 Termination unit, as you are probably aware, they are a different form factor, where the NICL01 is a module that mounts in a Termination Module Rack and the NTCL01 mounts on an NFTP01 Field Termination Panel. As long as you have room in the pane, or an adjacent cabinet where you can install the NTCL01 and you hvae jumper cables (e.g. NKTT01 if running coax loop), then you should not have an issue.
I do know that the ABB US company does have 6 of the NICL01 units in stock and it appears that they have 3 pre-owned units available as well, so, as you are outside of the US, perhaps you can have your local ABB office contact the Logistics Group at ABB US about buying them for you. Alternatively, you could try reaching out to them directly at partservices@us.abb.com, to see about how you might be able to buy an NICL01 from the US office. If they cannot sell to you directly, I am certain that they can help get you a quote from the ABB office in your area.
Good luck.
Rob Murphy
I do know that the ABB US company does have 6 of the NICL01 units in stock and it appears that they have 3 pre-owned units available as well, so, as you are outside of the US, perhaps you can have your local ABB office contact the Logistics Group at ABB US about buying them for you. Alternatively, you could try reaching out to them directly at partservices@us.abb.com, to see about how you might be able to buy an NICL01 from the US office. If they cannot sell to you directly, I am certain that they can help get you a quote from the ABB office in your area.
Good luck.
Rob Murphy