Facing field current and field voltage drop issue in DCS800?
We are facing problem of field current and field voltage drop issue .
We have changed the drive rating from DCS800-S02-0075-05 to DCS800-S01-0900-05 with Set type code .
According to Motor Data field current is 6.5 and when we are using internal field it shows 6.5 amp in CDP but in actual it shows 3.3 amp kindly give us the better solution .
We have changed the drive rating from DCS800-S02-0075-05 to DCS800-S01-0900-05 with Set type code .
According to Motor Data field current is 6.5 and when we are using internal field it shows 6.5 amp in CDP but in actual it shows 3.3 amp kindly give us the better solution .
Answers
From your words it can be understood that you have replaced the CON-4 board in a 900A converter. Is this right?
What about the PIN-4? The field current is measured in T100, depending on the wire loops. You should have ONLY one wire through the hole in T100.
What about the PIN-4? The field current is measured in T100, depending on the wire loops. You should have ONLY one wire through the hole in T100.